You need to close down on the non trv valves, they are normally lockshield and mostly fitted to the return side of the rad. Start with the ones closest to the boiler/pump, shut the valves down to 1 turn open, check that the dodgy rads are getting warm, if not then close down on the next rads until the furthest get hot. When you do this leave all of the trvs fully open! The last one I did required 80% of the rads to have the flow reduced, the nearest one to the pump was 1/2 a turn open.
Be warned you could end up with leaks if you "disturb" a very old valve, once you are happy then consider putting in scale inhibitor such as Fernox, especially if you have been draining parts of the system.
Good luck!